Reinforced Concrete Flat Slab per. Eurocode 2
Reinforced Concrete Flat Slab Design per. Eurocode 2
Flat slab design Flexure design Column strip and middle strip
EN 1992 Eurocode 2 applies to the design of buildings and other civil engineering works in plain, reinforced and prestressed concrete. It complies with the principles and requirements for the safety and serviceability of structures, the basis of their design and verification that are given in EN 1990: Basis of structural design. EN Eurocode 2 is concerned with the requirements for resistance, serviceability, durability and fire resistance of concrete structures.
Precision:
Input- Insert the dimensions of the slab span and section, loads with their respective safety factors and material properties of the concrete and the reinforcement steel.
Slab span
Span direction Span length
X direction (lx) m
Y direction (ly) m
Adjacent span in x axis m
Adjacent span in y axis m
Adjacent span should be greater than 0.85ly
Section
Slab depth (h) m
Column dimensions (x,y) m
m
Concrete cover m
Punching shear design
Column position
Load
Dead load kN/m2
Live load kN/m2
Material
Concrete grade
Flexural and shear rebar grade
Flexural and shear rebar size
Slap span strips
This application Requires Premium Membership to execute calculations
I am aware of the slab design is based on the concise Eurocode 2, Concise Table 15.3. According to Eurocode, the ratio of the adjacent span and design span is greater than 0.85 and the live load must be less than or equal to the dead load in order to use the coefficient method design from the Concise Table 15.3.
Output results - This will design a reinforced concrete flat slab for flexure and shear in the tables below from the design input data in the table above.
Design spans
Column strip width
m Middle strip
m
Design moments
Sagging moment
kN-m Column strip
kNm/m
Middle strip
kNm/m
Hogging moment
kN-m Column strip
kNm/m
Middle strip
kNm/m
Analysis
Design values Sagging moment Hogging moment
Column strip Middle strip Column Strip Middle strip
K value
Required steel area (As)
mm2/m
mm2/m
mm2/m
mm2/m
Bar spacing
mm
mm
mm
mm
Provided steel area (As)
mm2/m
mm2/m
mm2/m
mm2/m
Shear design values
Reaction force at the column (VED)
kN
Design shear stress at the face of the column (vED)
MPa
Concrete maximum shear strength (vRd,max)
MPa
Design shear stress at the control perimeter u1 (vED)
MPa
Concrete shear resistance (vRd,c)
MPa
Punching shear reinf. per perimeter (Asw)
mm2
No of punching shear reinf. provided (n)
Punching shear resistance with shear reinf. (vRd,cs)
MPa
Outer perimeter where shear reinf. not required (uout,ef)
m
Radius from the column face to the outer perimeter (r)
m
Punching shear layout
Punching shear section
Equation used for Flat slab design Flexure design Column
Browser does not support this operation
Alazar Woldeyohannes
Master's program in Structural Engineering in the School of Mechanical, Aerospace and Civil Engineering
University of Manchester
Email available on request