Thread: Excitation Transformer Sizing
    Aug 2014
    Can any one help me. I am preparing a calculation sheet for sizing an Exitation transformer, so far I have this
    Generator Data:
    Rated output: Sgn = 108 MVA
    Rated voltage: Un = 13.8 kV
    Rated frequency: f = 60 Hz
    Rated speed: n = 276.9 rpm
    Preliminary Assumed Excitation Data:
    Excitation power: Pfn = 540 kW | 0.5% Sn
    Rated excitation voltage: Ufn = 320 V | adopted value
    Rated excitation current: Ifn = 1687.5 A | Pfn/Ufn
    Maximum excitation voltage: Ufmax = 640 V | 2.0*Ufn
    Maximum excitation current: Ifmax = 1856.3 A | 1.1*Ifn
    Corresponding values on the ac-side:
    Uac = 547.4 V | 1.05*1.1*[?/(3?2)]*Ufmax
    Iac = 1515.6 A | ?(2/3)*Ifmax
    S = 1436.9 kVA | ?3*Uac*Iac
    Rated output: Sn = 1500 kVA | adopted value
    Rated voltage at LV side: Uac = 550 V | adopted value
    Rated current at LV side: Iac = 1574.6 A | Sn/(?3*Uac)
    Rated current at HV side: In = 62.8 A | Sn/(?3*Un)
    Rated CT ratio at HV side: 100/5 A | adopted value
    My question is if there is a method to calculate the Rated excitation voltage, normally this value is given by the manufacturer. But I need to know how they calculate this value.
    Thanks
    Newark, NJ
    238
    This is Residential Transformer Loading presentation.
    Transformer Sizing Presentation.pdf