Results 1 to 11 of 11
Thread: Electrical Panelboard Load Calculator
  1. #1
    Technical Fellow Kelly_Bramble's Avatar
    Join Date
    Feb 2011
    Location
    Bold Springs, GA
    Posts
    2,570
    ipt>
    This excel calculator will Determine following:
    Calculate Voltage / Voltage Difference of Each Phase
    Calculate Unbalanced Load in Neutral Wire.
    Calculate Expected Temperature rise in Each Phase.
    Calculate Load in Each Phase and Outgoing Feeders.
    Calculate Starting/Full Load/Continuous/Non Continuous Load
    Calculate Size of Cables for Each Outgoing Feeder.
    Exhaustive list of Engineers Edge Engineering Calculators.
    Read More: Electrical Panelboard Load Excel Calculator
    Download: Electrical Panelboard Load Calculator
  2. #2
    Associate Engineer
    Join Date
    Dec 2013
    Posts
    3
    lot of thanks for that file
    actual since more time I research for same that file
  3. #3
    Associate Engineer
    Join Date
    Jan 2014
    Posts
    1
    It keeps downloading a php file when I click your link for Electrical Panel Load Calculation(8-5-11).xls, why is this?
  4. #4
    Join Date
    Feb 2011
    Location
    Bold Springs, GA
    Posts
    2,570
    Quote Originally Posted by brett132 View Post
    The link is working for two of us...
    Are you logging in when trying to download?
    Are you "right clicking" and as ?
  5. #5
    Associate Engineer
    Join Date
    Mar 2014
    Posts
    1
    Thanks but no download
  6. #6
    Lead Engineer Cake of Doom's Avatar
    Join Date
    Aug 2012
    Location
    UK
    Posts
    433
    It opened fine for me. Are you using a program other than Excel/Office to open the .xls?
  7. #7
    Associate Engineer
    Join Date
    Jun 2014
    Posts
    1
    Dear Kelly.-
    Thaks a lot for your Excel, just a few comments:
    - Question: What about loads cennected to two phases
    - Mistake: Cell X24 fx =SI(M24="","",W24/AQ24) needs to be change for =SI(W24="","",W24/AQ24)
    Best regrats,
    Andres Bedon
  8. #8
    Associate Engineer
    Join Date
    Dec 2014
    Posts
    1
    Thanks
  9. #9
    Associate Engineer
    Join Date
    Apr 2015
    Posts
    1
    Thanks
  10. #10
    Associate Engineer
    Join Date
    May 2015
    Posts
    2
    Hey friends please tell me why Excel shows this error when a formula or function “UnBalance Neutral Current”.
    Help me please.
  11. #11
    Associate Engineer
    Join Date
    Dec 2015
    Posts
    2
    thanks and good job