Minimum Ventilation Rates in the Breathing Zone, Based on ANSI/ASHRAE Standard 62.1-2007
Occupancy
Human Outdoor
Air Rate, R
cfm/person
Area Outdoor
Air Rate, Ra
cfm/ft2
Occupant Density
(see Note 4)
#/1,000 ft2
Combined Outdoor
Air Rate
cfm/person
Air Class
Educational Facilities
Daycare (through age 4)
10
0.18
25
17
2
Classrooms (ages 5–8)
10
0.12
25
15
1
Classrooms (ages 9 plus)
10
0.12
35
13
1
Lecture classroom
7.5
0.06
65
8
1
Art classroom
10
0.18
20
19
2
Science laboratories
10
0.18
25
17
2
University/college laboratories
10
0.18
25
17
2
Wood/metal shop
10
0.18
20
19
2
Multi-use assembly
7.5
0.06
100
8
1
Office Buildings
Office space
5
0.06
5
17
1
Reception areas
5
0.06
30
7
1
Main entry lobbies
5
0.06
10
11
1
Miscellaneous Spaces
Electrical equipment rooms
0.06
1
Shipping/receiving
0.12
1
Warehouses
0.06
2
Public Assembly Spaces
Auditorium seating area
5
0.06
150
5
1
Libraries
5
0.12
10
17
1
Museums (children's)
7.5
0.12
40
11
1
Museums/galleries
7.5
0.06
40
9
1
Retail
Sales (except as listed below)
7.5
0.12
15
16
2
Mall common areas
7.5
0.06
40
9
1
Beauty and nail salons
20
0.12
25
25
2
Sports and Entertainment
Gym/stadium (play area)
0.3
30
2
Spectator areas
7.5
0.06
150
8
1
Health club/aerobics room
20
0.06
40
22
2
Gambling casinos
7.5
0.18
120
9
1
General Notes for Table:
1. Related requirements: The rates in this table are based on all other applicable requirements of ANSI/ASHRAE Standard 62.1-2007 being met.
2. Smoking: This table applies to no-smoking areas. Rates for smoking-permitted spaces must be determined using other methods.
3. Air density: Volumetric airflow rates are based on an air density of 0.075 lbda/ft3, which corresponds to dry air at a barometric pressure of 1 atm and an air temperature of 70°F. Rates may be adjusted for actual density but such adjustment is not required for compliance with the standard.
4. Default occupant density: The default occupant density shall be used when the actual occupant density is not known.
5. Default combined outdoor air rate (per person): This rate is based on the default occupant density.
6. Unlisted occupancies: If the occupancy category for a proposed space or zone is not listed, the requirements for the listed occupancy category that is most similar in terms of occupant density, activities, and building construction shall be used.
References