Pile Point-Bearing Capacity Formula and Calculator
Civil Engineering Application & Design Resources
Theoretical Pile Point-Bearing Capacity Equations and Calculator
The theoretical point-bearing capacity (also known as the tip resistance and point capacity), Qp, of a single pile can be calculated in much the same manner as for a footing. Since the pile size, B, is small, the (1/2) · γ · B · Nγ term is generally omitted.
Preview: Pile Point-Bearing Capacity Calculator
Eq. 1a,
SI Units
Qp = Ap ( 0.5 · ρ · g · B · Nγ + c · Nc + ρ ·g · Df · Nq )
Eq. 1b,
US Imperial units
Qp = Ap ( 0.5 · γ · B · Nγ + c · Nc + γ · Df · Nq )
For cohesionless (granular) soil, c = 0. For sands and silts, the tip point-bearing capacity increases down to a critical depth, Dc, after which it is essentially constant. For loose sands (i.e., with relative densities less than 30%) and loose silts, the critical depth is taken as 10B. For dense sands (relative densities above 70%), and dense silts, the critical depth is 20B. Between relative densities of 30% and 70%, the critical depth can be interpolated between 10B and 20B.
Eq. 2a
SI Units
cohesionless; D ≤ Dc
Qp = Ap · ρ · g · Df · Nq
Eq. 2a
US Imperial units
Qp = Ap · γ · Df · Nq
For cohesive soils with θ = 0°, Nq = 1 and the γ · Df term is approximately cancelled by the pile weight. Nc = 9 for driven piles of virtually all conventional dimensions. (See Table 1 and Table 2.)
Eq. 3
cohesive
Qp = Ap · c · Nc ≈ 9 · Ap · c
Where
Qp = capacity lbf, N
Ap = pile contact area ft2, m2
ρ = density, lbm/ft3, kg/m3
g = acceleration of gravity, ft/sec2, m/s2
B = diameter or width, ft, m
Nγ = capacity factor, Table 3
c = cohesion, lbm/ft2, kg/m2
Nc = capacity factor
Df = pile depth, ft, m
Nq
= capacity factor
γ = specific weight
Φ =
Table 1 Meyerhof Values of Nq for Piles*
Φ
25°
28°
30°
32°
34°
36°
38°
40°
42°
45°
driven
8
12
20
25
35
45
60
80
120
160
230
drilled
4
5
8
12
17
22
30
40
60
80
115
Table 2 Values of Nc for Driven Piles*
(square and cylindrical perimeters)
Df / B
Nc
0
6.3
1
7.8
2
8.5
≥ 4
9
Table 3
Terzaghi Bearing Capacity Factors
Φ
Nγ
0.0
0.5
10° 1.2
15° 2.5
20° 5.0
25° 9.7
30° 19.7
35° 42.4
40° 100.4
45° 297.5
Table 4
Recommended Values of Adhesion, (piles in clay)
Pile Type consistency cohesion, c
( lbf/ft2 (kPa) )
timber or concrete very soft 0–250 (0–12)
soft 250–500 (12–24)
medium stiff 500–1000 (24–48)
stiff 1000–2000 (48–96)
very stiff 2000–4000 (96–192)
steel very soft 0–250 (0–12)
*Significant variation in Nq has been reported by various researchers. The actual value is highly dependent on # and the installation method.
Derived from Foundations and Earth Structures Design Manual, NAVFAC DM-7.2, 1986, Fig. 2, p. 7.2-196.
Source
Civil Engineering Engineering Reference Reference Manual for the PE Exam for the PE Exam
Fourteenth Edition
Michael R. Lindeburg, PE