Wind Loading Analysis Simple Building - Engineers Edge
Open Wind Loading Analysis Calculator
WIND LOADING ANALYSIS - Main Wind-Force Resisting System er ASCE 7-98 Code for Low-Rise Buildings with h <= 30' and Roof q < 10 deg. Using Method 1: Simplified Procedure (Section 6.4)
For Method 1: Simplified Procedure (Sect. 6.1) to be used for an enclosed or partially enclosed low-rise building to determine the design winds, ALL of the following 7 conditions MUST BE met:
1. The building is a simple diaphragm building, in which wind loads
are transmitted through floor and roof diaphragms to the
vertical Main Wind-Force Resisting System (MWFRS).
2. The building roof angle q < 10 degrees.
3. The building mean roof height, h <= 30 ft.
4. The building is a regular shaped building, having no unusual
geometrical irregularity in spatial form.
5. The building is not classified as a "flexible" building, so it is
considered "rigid".
6. The building structure has no expansion joints or separations.
7. The building is not subject to topographic effects (Sect. 6.5.7),
thus Kzt = 1.0.